A property of the material, not of the part
Resistance belongs to a particular wire or component, while resistivity belongs to the material it is made from. For a uniform conductor, resistance equals resistivity times length divided by cross-sectional area. The SI unit of resistivity is the ohm meter (Ω·m). This hub has 17 converters, led by the Electrical resistivity converter, for ohm meters, ohm centimeters, microohm meters, microohm centimeters and ohm square millimeters per meter. Each tool takes a value, a source unit and a target unit, and returns the number in the target unit. Which unit appears in a table depends on the trade: physicists use ohm meters, semiconductor engineers use ohm centimeters, and electricians sizing cable use ohm square millimeters per meter.
The factors between the five units
Because a meter holds 100 centimeters, 1 Ω·m equals 100 Ω·cm, and the Ohm meters to Ohm centimeters converter multiplies by 100. A microohm meter is 10^-6 Ω·m, so 1 Ω·m is 1,000,000 µΩ·m. One microohm centimeter is 10^-8 Ω·m, which makes 1 µΩ·m equal to 100 µΩ·cm. The practical cable unit, ohm square millimeters per meter, has a neat property: 1 Ω·mm²/m equals exactly 10^-6 Ω·m, the same as 1 µΩ·m. So the Ohm square millimeters per meter to Ohm meters converter divides by 1,000,000, and its numerical value matches a microohm meter reading. Remembering that equality helps you check a table that mixes these units.
Typical values for common conductors
Annealed copper, the reference for the International Annealed Copper Standard, has a resistivity of 1.7241 × 10^-8 Ω·m at 20 degrees Celsius, which is 0.017241 Ω·mm²/m. Pure copper tested in modern conditions is often quoted near 1.68 × 10^-8. Aluminum is about 2.65 × 10^-8 Ω·m, silver about 1.59 × 10^-8, and iron about 9.7 × 10^-8. Resistance wire such as nichrome sits around 1.1 × 10^-6 Ω·m, which the Ohm meters to Microohm meters converter shows as 1.1 µΩ·m. Values depend on purity, work hardening and temperature, so a handbook figure applies to a stated condition. Use the number printed with the table as your starting point. The IACS convention itself deserves a note: it rates a conductor against annealed copper at 100 percent, so aluminum alloy 1350 comes out near 61 percent and brass near 28 percent. A conductivity percentage converts to resistivity by dividing 0.017241 Ω·mm²/m by the fraction, so a material at 61 percent has about 0.0283 Ω·mm²/m, a figure that the Ohm square millimeters per meter to Ohm meters converter writes as 2.83 × 10^-8 Ω·m.
Cable resistance, worked through
To find the resistance of 100 m of 1.5 mm² copper conductor, use R = ρL/A with the cable-friendly unit. With ρ = 0.0175 Ω·mm²/m, R = 0.0175 × 100 / 1.5 = 1.167 Ω. A current of 10 A through that conductor drops 11.7 V. A circuit with 100 m out and 100 m back doubles the length to 2.33 Ω, drops 23.3 V and wastes about 233 W as heat. The Ohm square millimeters per meter to Ohm meters converter turns 0.0175 into 1.75 × 10^-8 Ω·m if you need base units. This simple check shows why long runs call for larger cross-sections. Real cables are stranded and heat up under load, so the nominal figure is the starting point. Standards publish maximum conductor resistance per kilometer for each cross-section, and those values are slightly higher than the ideal solid-conductor calculation because strands lie in a spiral and the metal is not perfectly pure. For a 2.5 mm² conductor the ideal figure is 0.0175 / 2.5 = 0.007 Ω per meter, or 7 Ω per kilometer, and published limits sit a little above it. The comparison is a quick way to catch a unit slip in a spreadsheet.
Semiconductors and ohm centimeters
Silicon wafers are specified by resistivity in ohm centimeters because doping levels are chosen to hit a target. Heavily doped material is below 0.01 Ω·cm, typical device wafers run from about 1 to 20 Ω·cm, and very high-resistivity wafers used in radio-frequency devices exceed 1,000 Ω·cm. Intrinsic silicon at room temperature is about 2.3 × 10^5 Ω·cm, or about 2,300 Ω·m, which the Ohm centimeters to Ohm meters converter confirms. Four-point probe instruments measure sheet resistance first, then convert using the wafer thickness. Insulators fall at the far end, with glass and many plastics between 10^10 and 10^16 Ω·m, enough that the conversion to ohm centimeters adds two more zeros.
Soil, seawater and grounding design
Earthing engineers measure soil resistivity in ohm meters with a four-pin Wenner arrangement, because the value decides how many rods and what spacing a grounding system needs. Wet clay may be 10 to 50 Ω·m, ordinary loam 100 Ω·m or more, and dry sand or rock above 1,000 Ω·m. Seawater sits near 0.2 Ω·m, far below the resistivity of fresh water, which is hundreds of ohm meters or more. A site report might list 150 Ω·m, which the Ohm meters to Ohm centimeters converter writes as 15,000 Ω·cm for a geotechnical table. Resistivity swings with moisture and season, so repeat readings are standard practice. The tools convert units and leave the design rules to the applicable earthing standard.
Temperature and the difference from conductivity
Metals gain resistivity as they warm. Copper rises by about 0.39 percent per degree Celsius, so a coil measured at 20 degrees Celsius reads roughly 16 percent higher at 60 degrees. Semiconductors move the other way, because heat frees more charge carriers. The reciprocal of resistivity is conductivity, in siemens per meter, and the separate conductivity topic on this site covers those units. Remember that 100 percent IACS corresponds to 58 MS/m, which is 1/58 Ω·mm²/m, or 0.017241. Do not enter a conductivity into a resistivity tool, since the result would be inverted. The unit labels tell you which topic applies: Ω·m is resistivity, S/m is conductivity.
Picking the right tool among 17
Read the title as source, then target. The pairs involving ohm square millimeters per meter are the ones to use when working with wire tables, and those involving microohm centimeters appear in metallurgy handbooks, where values such as 1.7 µΩ·cm for copper are common. A quick check: 1 Ω·mm²/m is 1 µΩ·m, 100 µΩ·cm and 10^-6 Ω·m. If a conversion produces a number off by 10,000, the centimeter and meter lengths were probably mixed up, since the area of a square meter is 10,000 times that of a square centimeter. Name the unit beside each figure while you work and the pattern becomes easy to follow. These tools only change the unit of a resistivity value. They do not account for temperature, alloy variation or cable construction, and they do not judge whether a conductor is suitable for a given current. A resistivity quoted for a thin film can also differ from the bulk value, since surface scattering raises it once the film thickness approaches the electron mean free path, which is why thin copper interconnects in chips are more resistive than the handbook figure.
Frequently asked questions
- How many ohm centimeters is one ohm meter?
- 100. One meter is 100 centimeters, so 1 Ω·m equals 100 Ω·cm.
- Is Ω·mm²/m the same as µΩ·m?
- Numerically yes. Both equal 10^-6 Ω·m, so converting between them leaves the number unchanged.
- What is the resistivity of copper?
- About 1.72 × 10^-8 Ω·m at 20 degrees Celsius for annealed copper, or 0.01724 Ω·mm²/m.
- Do these tools calculate wire resistance?
- No. They convert resistivity units. Use R = ρL/A yourself, with the length and area in matching units.